The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th , 2014”

Upload: marilynn-gray

Post on 24-Dec-2015

219 views

Category:

Documents


2 download

TRANSCRIPT

Page 1: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

The Fall Builders’ ForumPart 9 Energy Efficiency and

Ventilation Regulations“Effective December 19th, 2014”

Page 2: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Builders’ Forum Introduction (5 min)• Overview of Changes (5 min)• Envelope (15-20 min)• HVAC / SWH (5-10 min)• 9.32 – Ventilation (15 min)• Compliance Options (10 min)• Closing Remarks (10 Min )• Additional Questions

Page 3: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

BCBC Energy Requirements(current to December 18, 2014)

• Part 9 (Houses and Small Buildings)• Prescriptive Insulation tables• EnerGuide 77• No requirement for professionals• Part 10: Energy Efficiency current requirements

Page 4: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

BCBC Energy Requirements(current to December 18, 2014)

Page 5: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

BCBC – December 19th, 2014

• Current Part 9 Insulation tables (Table 10.2.1.1.A & Table 10.2.1.1.B) deleted

• Current reference to EnerGuide 77 deleted

• New admin section 2.2.8. sets out Information required for energy compliance by performance path

5

Page 6: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Prescriptive path– In-cavity Insulation Table

Performance path– EnerGuide model – 77

Prescriptive path– Effective RSI-value Table– Trade-off Options – with /

without HRV

Performance path #1– EnerGuide model – better

than reference building

Performance path #2– NECB

Current to Dec. 18, 2014 As of Dec. 19, 2014

Compliance PathsSingle Family Home

Page 7: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

December 19th, 2014

• New insert to Section 9.32. Ventilation• New Section 9.36. Energy Efficiency

– Incorporates NBC 9.36. as a new section of the BC Code

• Current Section 9.36. (Secondary Suites) becomes 9.37.

• Section 9.37. Objectives and Functional Statements– Renumbered to 9.38.

7

Page 8: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

BCBC Energy Requirements(as of December 19, 2014)

Page 9: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Mid-stream amendment to the 2012 BC Building Code developed by the NRC.

• ~110 pages• Largest Code change in the history of

the BC Building Code• Multiple pathways to compliance

– Several options for specific building types– ‘Systems approach’ to prescriptive req’s– Performance-based options available

What is Section 9.36?

Page 10: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Treats the building as a system

• Enables performance-based design

• Removes barriers for new technologies

The GREEN of Section 9.36

Page 11: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Additional attention to detail at design stage• Possible expansion of design team to include

all sub trades now• A whole new Code to purchase, understand,

and apply (NECB)• Additional items in Building Permit submission• A new normal

What It MeansFor Designers / Builders

Page 12: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36. Scope & Application

9.36.1.1. Scope This section is concerned with the energy used by buildings through

– The building envelope heat losses (9.36.2), – Heating/ ventilation systems (9.36.3), (9.32), and– Domestic hot water (9.36.4)

12

Page 13: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

The Building Envelope

BCBC 9.36.2

Page 14: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Focus is on total building performance, not just thermal insulation anymore

• Heat transfer and air leakage between conditioned space and unconditioned space

• Windows must conform to Section 9.7• Properties of insulation, location and installation

of air barriers, and vapour barriers must conform to Section 9.25

Scope + ApplicationBuilding Envelope

Page 15: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36. Energy Efficiency

Nominal Insulation

Page 16: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective Insulation

9.36. Energy Efficiency

Insulation in the framing cavity achieves continuity of effective Insulation, and is only a component in the assembly.

Page 17: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Climate Zones

17

Page 18: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Prescriptive path: Requirements vary whether or not an HRV is installed• Table with minimum effective RSI-values

• Look-up tables for most common assemblies, and information on how to calculate them and others are provided in the Appendix

• Breaking each wall apart to individual components

9.36.2.6. Thermal Characteristics of Above Ground Opaque Assemblies

Page 19: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective RSI-values – without HRV

9.36.2.6. Thermal Characteristics of Above Ground Opaque Assemblies

Table 9.36.2.6.A

Page 20: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective RSI-values – with HRV

9.36.2.6. Thermal Characteristics of Above Ground Opaque AssembliesTable 9.36.2.6.B

Page 21: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Example:• Wall 1: 170 m2

• 2x6 @ 16” o/c, R-19 batt insulation; gyp bd. inside, plywood sheathing, rain screen, cement stucco:

• From table A-9.36.2.6.(1)A:• 2x6 @ 16” o/c, R-19 batt insulation effective R-value = 2.36• Additional layers (values from Table A.9.36.2.4.(1) D

• Interior air film 0.12• Gyp bd. 0.08• Ply sheathing 0.10• Rain screen cavity 0.15• Stucco 0.08 • Exterior air film 0.03• Total: 0.50

• Total effective RSI = 2.86 This wall assembly will work in Zone 4

Wall Assembly Calculation Example

Page 22: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Major structural penetrations through assemblies are permitted – but total area must not exceed 2%• Major allowable penetrations include balcony slabs,

beams, columns, and minor ornamental structural elements.

• Minor penetrations include Pipes, ducts, through-wall equipment vents are not considered in the 2%.

9.36.2.4. Calculation of Effective Thermal Resistance of Assemblies

Page 23: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36.2.4. Calculation of Effective Thermal Resistance of Assemblies

RSIeffective vs. RSInominal RSIeff = RSInom

Page 24: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective R-Value

Page 25: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective R-Value

Page 26: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Effective R-Value• Look-up tables for common assemblies, and

information on how to calculate others (9.36.2.4)• Calculator - Canadian Wood Council – Wall Thermal

Design Calculator

Page 27: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Continuity of Insulation

Page 28: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Insulation must be continuous across the entire envelope – but this does not mean continuous insulation across face.

• Another measure to reduce Thermal Bridging

• Applies to building components such as partitions, chimneys, fireplaces, and columns and beams along exterior walls, but not to stud framing and ends of joists (accounted for by effective R-value calculation).

Continuity of Insulation

Page 29: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36.2.5. Continuity of Insulation

• 9.36.2.5. (7) ducts, plumbing pipes, electrical or communication conduits placed within the insulated portion of a floor or ceiling assembly must have an effective insulation level not less than RSI 2.78 (R-15.78).

• This applies to attics, unheated crawlspaces, etc.

Page 30: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36.2.5. Continuity of Insulation

• Ducts outside the heated envelope must be insulated to the same effective insulation level as required for walls above grade

Page 31: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Alternative to placing ducts outside the heated building envelope: insulating the attic and making it conditioned space.

• Point to remember: The insulated roof section will now have to be the RSI value for your Zone. (cathedral)

9.36.2.5. Continuity of Insulation

Page 32: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Continuity of Insulation

Page 33: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Unheated floor slabs must be insulated min. 1.2m horizontally or vertically down from its perimeter, with a thermal break along edge of slab a min. 50% of required insulation

9.36.2.8. Assemblies In Contact With Ground

Page 34: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Airtightness

Page 35: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• 9.25 currently requires an airtight building envelope• 9.36 addresses construction of air barrier details

because of the heat loss implications.• Testing is NOT required.• Air barriers must be continuous:

• across joints,• between assemblies, and• around penetrations.

Airtightness

Page 36: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Joints in panel-type air barrier materials must be sealed by:• Caulking, • Sealants,• Spray foam• Gaskets• Tapes

Airtightness

Page 37: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Flexible sheet air barrier materials require all joints to be:• lapped at least 50 mm (2”)Not 11/2”,

and structurally supported• sealed, and • structurally supported

Sealants must be non-hardening

Page 38: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Airtightness

Page 39: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

HVAC + Service Water Heating

BCBC 9.36.3 + BCBC 9.36.4

Page 40: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Heating systems must be designed in accordance with good practice (as per 9.32 & 9.33)

• Systems not referenced in 9.36 must be designed in accordance with requirements of the NECB

• Heating and air-conditioning equipment must be located inside the conditioned space, unless it is designed to be located outside

• Equipment efficiency set out in Table 9.36.10 (HVAC) and Table 9.36.4.2 (Service Water Heating)

HVAC + Service Water Heating

Scope + Application

Page 41: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• All piping/ducts must be located inside the conditioned space.

• If located outside or within an exterior wall, the piping/ducts must be insulated to same level as required for above grade walls

Continuity of Insulation

HVAC + Service Water Heating

Page 42: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ducts outside the heated envelope, or within an exterior assembly:• All joints in the ducts must be

sealed with sealant, mastic, or foil faced tape

• Fabric duct tape is not permitted

Continuity of Air Barrier

HVAC + Service Water Heating

Page 43: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Heat pumps with supplementary heaters – controls should prevent operation of supplementary heater when the heat pump can supply the full heat load

• Heating & cooling systems with separate controls must prevent both cooling & heating to be activated simultaneously

• Heating and air conditioning equipment must be located inside a conditioned space, unless it is designed to be installed outside.

Temperature Controls

HVAC + Service Water Heating

Page 44: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• The first 2 m of piping from a storage tank or heater must be insulated with pipe insulation

• If hot water piping system has recirculation, the entire system must be insulated.

• If piping is located outside the heated envelope, it must be insulated to no less than the effective R-value of exterior walls.

Hot Water PipingHVAC + Service Water Heating

Page 45: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation

BCBC 9.36.3.9 + BCBC 9.32

Page 46: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Exhaust only ventilation acceptable• New Principal Fan Sizing Rule• Ventilation air must be distributed to each bedroom and

a common area• 4 acceptable options• Principal System –must run continuously• Crawlspace Ventilation Required• Credit for very short bath fan exhaust ducts

Ventilation

Scope + Application

Page 47: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation Principal Ventilation System Exhaust Fan

• Based on bedroom count & square footage• Minimum exhaust fan air-flow rate in Table 9.32.3.5

Page 48: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation Kitchen & Bath Fans

• Principal exhaust fan capacity @ 50 Pascals• Designed to run continuously• Controlled by dedicated switch

• Clearly marked “principal Ventilation Exhaust Fan”

• Two settings: on & off

• Accessible for servicing

• If capable of running at multiple flow rates, must have a separate switch so low rate is not less than required

• Sound rating not to exceed 1.0 sone

Page 49: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation Kitchen & Bath Fans

• Exhaust must be installed in every kitchen and bathroom

• Unless these are served by principal ventilation system, the Minimum flow rate is as per Table 9.32.3.6

Page 50: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Principal exhaust fan sized to Table 9.32.3.5; continuous operation

• Furnace fan must run continuously

• Supply air drawn into furnace return; limits on supply duct

9.32.3.4 (2) Supply with Forced Warm Air Heating

Page 51: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.32.3.4 (3) HRV Supply with Forced Warm Air Heating

Page 52: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.32.3.4 (4) Independently Distributed HRV System

• Dedicated supply ducts to each bedroom and to each floor

• At least one exhaust located 2 m above upper floor

Page 53: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation

Page 54: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation

Page 55: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

• Only applicable to one storey dwelling (<168 m2 with no forced air heating)

• Passive inlets must be a min. 1.8m above floor

• Each bedroom must have one inlet with unobstructed vent area of 100 mm diameter

• At least one common area must have an inlet

9.32.3.4 (6) Passive Supply

Page 56: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation 9.32.3.7 Heated crawlspace ventilation

• If crawlspace is heated by ducted forced air heating, it must be connected to floor above by at least one transfer grille (25cm2) for each 30m2 of crawlspace area

Note: Crawlspace ventilation in this section must not be confused with exterior ventilation of unheated crawlspace

Page 57: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation

9.32.3.8 Ducts

• Exhaust and supply ducts:• Must be sized as required by manufacturer &

equivalent diameter as per Table 9.32.3.8 (3)• Need to be air-sealed • Insulated & provided with vapour barrier

Page 58: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Ventilation Future standard

Page 59: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Compliance

Part 9 Building Energy Regulations in BC

Page 60: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Review of 9.36Part 9 Building Energy Regulations in BC

Effective December 19, 2014

Page 61: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

ComplianceRequirements for all Pathways

Design Verification ReportDrawing Submission

Page 62: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Envelope section drawing(s) to indicate Prescriptive requirements found in the Tables 9.36.2.6.A/B and Tables 9.36.2.8. A/B. Show all envelope insulation and components with notes indicating the Effective Thermal Resistance (RSI) Value of the Assembly. Both above and below grade.

If you have a feature wall then you will be required to show all of your wall assembly for this wall as well the other three typical assemblies.

ComplianceRequirements for all Pathways

Page 63: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

ComplianceRequirements for all Pathways

Window section drawing(s) to indicate Prescriptive requirements found in Tables 9.36.2.7.A./B./C.

Show all Fenestration, Doors, and Skylights with notes indicating the Overall Thermal Transmittance (U Value)

These are separate labels from the NAFS labels on windows now.

Page 64: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36. Energy Efficiency

Page 65: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

Compliance

• Drawing(s) to indicate Prescriptive requirements found in Table 9.36.3.10 and Table 9.36.4.2. Show all systems and types.

• This will include Space heating, Space cooling, and Service hot water.

• The notes on the plans will have to indicate the Performance Rating and Energy Source.

Page 66: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

What is expected on the plans

• Completed information on the plans to confirm compliance

• Wall/ceiling assembles, with complete breakdown of the Effective RSI value

• Doors and windows indicated with the appropriate U-Values

• All heating and service water appliances are to be indicated on the plans

Page 67: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

What to Expect from the municipality

• Building permit processing time will be increased accordingly to the permit and complexity to confirm compliance

• More inspections required by the Municipality for the first period of implementation of the new Code

• Training to the community provided by the Municipality to create a seamless cross over into the new Code

Page 68: The Fall Builders’ Forum Part 9 Energy Efficiency and Ventilation Regulations “Effective December 19 th, 2014”

9.36 Energy Efficiency

• Questions?